I'm working on some numbers for cyberinfrastructure for Compute Canada. I am not currently doing single point localization microscopy but we plan to get into it.
I just wonder is there a consensus in the field if the raw images for each point localization have to be retained for 7 years or are people just keeping the localization data? When I do these calculations I get the following so it seems impossible with existing infrastructure to retain the raw data.
2000 x 2000 pixel camera and 16-bit images = 2000x2000x16 = 64 MB per image
10,000 frames for single molecule imaging and two colour super resolution
10,000x2x64 = 1.28 TB
4 conditions, 10 images per condition, experiment done in triplicate
1.28 TBx4x10x3 = 154 TB per experiment
So I'm guessing people are not keeping the raw data or I made a mistake in my calculations.
Looking forward to some feedback!
Sincerely,
Claire