|   | 
		Dear Listers,
 I'm doing a set of experiments which requires high magnification (60x objective + x36 pan zoom) on our confocal Olympus FV1000. the microscope is placed on the air table, which do not touch any wall or tables around. Imaging was going well, but at some point I started to see a zigzag pattern in the scanning, similar to that one gets when the air table is lucking nitrogen. This seems not to be a problem of the scanner itself, using a separate scanning unit delivers the same zigzag. The lab is on the 7th floor, but this shouldn't be the case as for about a month the imaging was going well. I'm wondering what could be a source of this problem in a typical lab, and what could be done to overcome it. Thank you in advance, Vladimir Ghukasyan | 
|    | Periasamy, Ammasi (ap3t) | 
|   | 
		Vladimir
 Seventh floor is not a good place for a microscopy system. If someone somewhere banging the wall or drilling in the building, the unit may pick up the vibration. Or make sure there is no autoclave or any high voltage unit is operating in the same electrical line coming to your microscopy room. Do you have the UPS for the confocal unit? The suggestion is get down to the basement or first floor!! Prof. Ammasi Periasamy Director, Keck Center for Cellular Imaging (KCCI) Professor of Biology and Biomedical Engineering Biology, Gilmer Hall (064), 485 McCormick Rd University of Virginia Charlottesville, VA 22904 Voice: 434-243-7602 (Office); 982-4869 (lab) Fax:434-982-5210; Email:[hidden email] http://www.kcci.virginia.edu/Contact/peri.php ************************ 10th Annual Workshop on FRET Microscopy, March 8-13, 2011 http://www.kcci.virginia.edu/workshop/workshop2011/index.php ************************* -----Original Message----- From: Confocal Microscopy List [mailto:[hidden email]] On Behalf Of Vladimir Ghukasyan Sent: Tuesday, August 10, 2010 3:59 PM To: [hidden email] Subject: Scanner and vibrations Dear Listers, I'm doing a set of experiments which requires high magnification (60x objective + x36 pan zoom) on our confocal Olympus FV1000. the microscope is placed on the air table, which do not touch any wall or tables around. Imaging was going well, but at some point I started to see a zigzag pattern in the scanning, similar to that one gets when the air table is lucking nitrogen. This seems not to be a problem of the scanner itself, using a separate scanning unit delivers the same zigzag. The lab is on the 7th floor, but this shouldn't be the case as for about a month the imaging was going well. I'm wondering what could be a source of this problem in a typical lab, and what could be done to overcome it. Thank you in advance, Vladimir Ghukasyan | 
|   | 
				In reply to this post by Vladimir Ghukasyan
			 
		Could that be due to placement of the scope near power lines (or some other large pice of electrical equipment) with a strong EMF that mess up the scanner galvos? Was there any recent electrical work done near the lab in the last month? Maybe the problem has always been there but you didn't notice it until you started using such high magnification?
 John Oreopoulos On 2010-08-10, at 3:58 PM, Vladimir Ghukasyan wrote: > Dear Listers, > > I'm doing a set of experiments which requires high magnification (60x > objective + x36 pan zoom) on our confocal Olympus FV1000. the > microscope is placed on the air table, which do not touch any wall or > tables around. > Imaging was going well, but at some point I started to see a zigzag > pattern in the scanning, similar to that one gets when the air table > is lucking nitrogen. This seems not to be a problem of the scanner > itself, using a separate scanning unit delivers the same zigzag. > > The lab is on the 7th floor, but this shouldn't be the case as for > about a month the imaging was going well. > > I'm wondering what could be a source of this problem in a typical lab, > and what could be done to overcome it. > > Thank you in advance, > Vladimir Ghukasyan | 
|   | 
				In reply to this post by Vladimir Ghukasyan
			 
		Some time ago I asked a similar question for Olympus 500. Our zigzagging was definitely not due to vibrations. We never figured out what it was, at some point (after Olympus for the fifth time took everything apart and put back together) it stopped. Good luck!
 Mike -----Original Message----- From: Confocal Microscopy List [mailto:[hidden email]] On Behalf Of Vladimir Ghukasyan Sent: Tuesday, August 10, 2010 3:59 PM To: [hidden email] Subject: Scanner and vibrations Dear Listers, I'm doing a set of experiments which requires high magnification (60x objective + x36 pan zoom) on our confocal Olympus FV1000. the microscope is placed on the air table, which do not touch any wall or tables around. Imaging was going well, but at some point I started to see a zigzag pattern in the scanning, similar to that one gets when the air table is lucking nitrogen. This seems not to be a problem of the scanner itself, using a separate scanning unit delivers the same zigzag. The lab is on the 7th floor, but this shouldn't be the case as for about a month the imaging was going well. I'm wondering what could be a source of this problem in a typical lab, and what could be done to overcome it. Thank you in advance, Vladimir Ghukasyan | 
|   | 
				In reply to this post by Vladimir Ghukasyan
			 
		Good evening,
 unfortunately, not an unknown problem to us as to many others. In two cases - an old style "TCS-SP" by Leica and an "FV300" by Olympus -, the pattern was the consequence of vibrations being transferred from parts of the systems including fans to the optical tabletop by way of stiff cables connecting the namely parts of the system to the actual scanner head. In both cases, we got rid of it by making sure that the cables were channeled through some holders including the kind of "air pads", which one uses to protect sensitive products in transportation boxes. I beg your pardon for my ignorance in English, I do not know the proper expression for these pads. Another case was with an old Sarastro p4d. There, the main fan providing the air for the forced ventilation of the laser managed to establish a standing acoustical wave in the lab. Since the air was pressed through a long, soft and flexible tube, it was possible to place the fan outside the lab and the problem vanished. Best wishes, Johannes -- P. Johannes Helm, M.Sc. PhD Seniorengineer CMBN University of Oslo Institute of Basic Medical Science Department of Anatomy Postboks 1105 - Blindern NO-0317 Oslo Voice: +47 228 51159 Fax: +47 228 51499 WWW: folk.uio.no/jhelm > Dear Listers, > > I'm doing a set of experiments which requires high magnification (60x > objective + x36 pan zoom) on our confocal Olympus FV1000. the > microscope is placed on the air table, which do not touch any wall or > tables around. > Imaging was going well, but at some point I started to see a zigzag > pattern in the scanning, similar to that one gets when the air table > is lucking nitrogen. This seems not to be a problem of the scanner > itself, using a separate scanning unit delivers the same zigzag. > > The lab is on the 7th floor, but this shouldn't be the case as for > about a month the imaging was going well. > > I'm wondering what could be a source of this problem in a typical lab, > and what could be done to overcome it. > > Thank you in advance, > Vladimir Ghukasyan > | 
|   | 
				In reply to this post by Vladimir Ghukasyan
			 
		Vladimir, I am trying to solve a similar problem.
 Largest improvement so far was the replacement of the fans that were cooling the electronics in the confocal scan unit. Often it is possible to halt the fans while continuing with the imaging to test which one is causing most of the vibrations. One can lower the speed of DC-fans by placing a resistor in series with the motor. If there are no fans in equipment that is mechanically connected to your microscope then this should cause your problem. You should remove any equipment that has fans or vibrating parts from the optics table and place it underneath or on racks above the table (racks should not be mounted to the table). For example it is not a good idea to add a computer that controls other components of your setup and place it onto the table. That would defeat the purpose of the floating table. The scanner's control electronics can also oscillate and it is not trivial to adjust its control loop to reduce the vibrations. It should not be necessary to do that as you system was optimized at the factory. However if for example the heater for the position sensor in your scanner feedback loop fails, it might start to oscillate. I heard that the vibrations might also vary with the pressure and extensions of the air cylinders in the legs in your table. It might be worth checking if the pressure gages match the recommended settings. I am less convinced that magnetic field pickup is an issue. Also if you have a good air table it should isolate vibrations from other activities in the building. You could check for this by measuring at 2 am when traffic in and outside the building is low and most equipment is off. If the vibrations are gone you might need to add additional dampers below the legs of your table. The legs of your table are a low pass filter. If you put two filters in series, suppression should add. I believe there are floor elements one can install in addition to an air-table. That could be cheaper than relocating your equipment. If one leg is not floating, the other three can not compensate for it. Your table manual would state how to correct for this. Urs Utzinger University of Arizona -----Original Message----- From: Confocal Microscopy List [mailto:[hidden email]] On Behalf Of Vladimir Ghukasyan Sent: Tuesday, August 10, 2010 12:59 PM To: [hidden email] Subject: Scanner and vibrations Dear Listers, I'm doing a set of experiments which requires high magnification (60x objective + x36 pan zoom) on our confocal Olympus FV1000. the microscope is placed on the air table, which do not touch any wall or tables around. Imaging was going well, but at some point I started to see a zigzag pattern in the scanning, similar to that one gets when the air table is lucking nitrogen. This seems not to be a problem of the scanner itself, using a separate scanning unit delivers the same zigzag. The lab is on the 7th floor, but this shouldn't be the case as for about a month the imaging was going well. I'm wondering what could be a source of this problem in a typical lab, and what could be done to overcome it. Thank you in advance, Vladimir Ghukasyan DISCLAIMER: This email and any files transmitted with it are confidential and intended solely for the use of the individual or entity to whom they are addressed. If you have received this email in error please notify the system manager. This message contains confidential information and is intended only for the individual named. If you are not the named addressee you should not disseminate, distribute or copy this e-mail. | 
|   | 
		We have had a similar result with an older UltraView spinning disc system.  After we removed everything possible from the light table and stood everything else on small squares of vibration-isolating carpet pad our vibration issues went down dramatically.  Our room was underground and isolated from power lines and other common EM interference, so your mileage may vary.  
 All the best, Tim Feinstein University of Pittsburgh On Aug 10, 2010, at 9:57 PM, Urs Utzinger wrote: > Vladimir, I am trying to solve a similar problem. > > Largest improvement so far was the replacement of the fans that were cooling > the electronics in the confocal scan unit. Often it is possible to halt the > fans while continuing with the imaging to test which one is causing most of > the vibrations. One can lower the speed of DC-fans by placing a resistor in > series with the motor. If there are no fans in equipment that is > mechanically connected to your microscope then this should cause your > problem. > > You should remove any equipment that has fans or vibrating parts from the > optics table and place it underneath or on racks above the table (racks > should not be mounted to the table). For example it is not a good idea to > add a computer that controls other components of your setup and place it > onto the table. That would defeat the purpose of the floating table. > > The scanner's control electronics can also oscillate and it is not trivial > to adjust its control loop to reduce the vibrations. It should not be > necessary to do that as you system was optimized at the factory. However if > for example the heater for the position sensor in your scanner feedback loop > fails, it might start to oscillate. > > I heard that the vibrations might also vary with the pressure and extensions > of the air cylinders in the legs in your table. It might be worth checking > if the pressure gages match the recommended settings. > > I am less convinced that magnetic field pickup is an issue. Also if you have > a good air table it should isolate vibrations from other activities in the > building. You could check for this by measuring at 2 am when traffic in and > outside the building is low and most equipment is off. If the vibrations are > gone you might need to add additional dampers below the legs of your table. > The legs of your table are a low pass filter. If you put two filters in > series, suppression should add. I believe there are floor elements one can > install in addition to an air-table. That could be cheaper than relocating > your equipment. If one leg is not floating, the other three can not > compensate for it. Your table manual would state how to correct for this. > > Urs Utzinger > University of Arizona > > -----Original Message----- > From: Confocal Microscopy List [mailto:[hidden email]] On > Behalf Of Vladimir Ghukasyan > Sent: Tuesday, August 10, 2010 12:59 PM > To: [hidden email] > Subject: Scanner and vibrations > > Dear Listers, > > I'm doing a set of experiments which requires high magnification (60x > objective + x36 pan zoom) on our confocal Olympus FV1000. the microscope is > placed on the air table, which do not touch any wall or tables around. > Imaging was going well, but at some point I started to see a zigzag pattern > in the scanning, similar to that one gets when the air table is lucking > nitrogen. This seems not to be a problem of the scanner itself, using a > separate scanning unit delivers the same zigzag. > > The lab is on the 7th floor, but this shouldn't be the case as for about a > month the imaging was going well. > > I'm wondering what could be a source of this problem in a typical lab, and > what could be done to overcome it. > > Thank you in advance, > Vladimir Ghukasyan > > > DISCLAIMER: This email and any files transmitted with it are confidential and intended solely for the use of the individual or entity to whom they are addressed. If you have received this email in error please notify the system manager. This message contains confidential information and is intended only for the individual named. If you are not the named addressee you should not disseminate, distribute or copy this e-mail. | 
| Free forum by Nabble | Edit this page | 
 
	

